QUESTION
I have a 540 ton 480VAC 3 PH Y-D closed transistion starter fed from a Y solidly grounded transformer secondary.
The complaint is that the chiller may experience a ground fault trip on the first start-up after not running for a long period of time. The gfi is reset and the chiller starts and runs. This problem has been happening for years.
When I took a first look at the starter I found that there is a zero sequence (core balance) CT on the line side of the main mold case non automatic breaker. This main is fitted with a shunt trip operated by the GFI relay.
The issue that I want to get your opinion on is this:
The installing contractor ran the the phase conductors and the Ground conductor through the CT. There is no Neutral conductor.
I am thinking that the ground conductor is not to be running through the ct and could be causing the problem.
REPLIES
tremblay.robin (unclebob)
Exactly, no ground conductor should run through the CT.