Clip Angle Weld

Can anyone point me in the direction for a detailed weld calculation for the clip angle to web connection for the attached?

Connection_Bolted.pdf (25.1 KB)

Thanks

Dik

Did you check Blodgett?

1 Like

Yup… but will check again, may have missed it… great book but missing an index.

Dik

@dik Blodgett section 5.4-3 discusses this. I refer to a procedure I learned from a professor I had in school when I’m working on these type connections of any significance. I’ve attached a scan of it.
I think it follows the example in Salmon & Johnson’s Steel Structures. Also attached that example.
Example.pdf (172.4 KB) S&J Example.pdf (592.2 KB)

1 Like

Thank you so much… I’ll take a look at them. I found the stuff in Blodget… I’d missed it the first glance. It’s a guide, but not quite to LRFD level. Again, thanks.

Dik

@bootlegend The larger example file is great… thanks… just what I was looking for.

Dik

Again… missed it the first time.

Thanks,

Dik

You are welcome.

No worries Dik.

Happens more often than I care to admit… now.

It happens to us all…

Dik

@bootlegend

Solved the problem… thanks