QUESTION
I am involved in a project which consists on a 10 ft excavation to place 3 ft diameter pipe.
Anyone knows if there is an approach of computing the setback so the overexcavated soils do not become a surcharge for the excavation (excavated walls)?. I am not familiar with this.
REPLIES
fattdad
Do a Culman analysis?
Make sure it’s at least 14 ft away (5 ft plus 10 cos 30). That’d be the active wedge plus 5 ft (phi of 30).
Not sure what else we can say?
Well, you can look at the OSHA stuff too.
PEinc