QUESTION
I am perplexed. I’m Inspecting a deck that a home inspector requested a structural evaluation be done by an engineer. The deck is 27 years old (two stories with 4x6 post), but has been well kept (very well kept). I see all sorts of problems related to current codes: 2x8 @ 24-inch joist with an 11 foot span, 1/2-inch (assume through) bolts at 48-inches oc on the ledger, no knee bracing …. The problem is the deck is solid and has been working fine for 27 years. No signs of distress. I know that since it is existing, it needed to meet the code at the time that it was built (which I don’t have but I doubt would have been much different; I’m pretty current on the last 15 years).
The deck is solid, plumb and true (which I was surprised by). Jumping up and down, you really feel minimal movement. I have seen much worst.
The deck is solid, but how can I state that (seal it) when I know it is out of spec. I can’t believe it is as old as it is, the thing looks great. I have problem changing up things (and costing the owner big bucks ) that evidently have worked for the life of this deck. Based on the current up keep, I would not be surprised if they got another 20 years out of this deck. I am amassed at how solid it felt and looked.
How can I say its OK?
REPLIES
Msquared48
Here are a few thoughts…
-
With the deck at 27 years old, the lumber could be 1.625 X 7.5 domension, or even rough cut members, although I doubt it.
-
The grade used would have to have been around 1500 psi in bending for the span and load to work.
-
With no knee braces, the lateral could be easily handled or upgraded with 2X4 flat diagonals below the joists, with tension ties at the extremities back to the residence.
-
Are the 4X6 posts embedded in concrete pilasters making the structural foundation a pole structure? In other words, is there continuity at the foundation?
-
The ledger connection could definitely be an issue. Just make sure the ledger is not inset and actually bearing on the wall - then there would likely be no issue.