QUESTION
We have to install UV dryers in the U.S.A.
In Europe, 3 phase + ground (Y) is common in industrial sites. Phase to phase around 400 VAC, ground to phase 230 VAC.
What is common in the U.S.A. One hears, 480 VAC delta, no ground?
Is there a standard?
REPLIES
rbulsara
For systems 600V and less:
Most common in the USA is 480Y/277 , 3phase, 4 wire grounded system for equipment in commercial and industrial sytems. Commercial lighting normally is 277V.
Convenience outlets, whether residential, commercial or industrial are always 120V, a part of 208Y/120V, Y system. Therefore, a system of step-down transformers , 480V delta to 208Y/120V is always present in commercial and industrial systems.
As with any other place, exceptions are always present which include ungroundned or groudned delta systems. Always check with your clients.
And for your further informatin:
Resiential systems are normally fed by 2 phases and a neutral (single phase, 3 wire) which in fact is part of a 208Y/120V , Y grounded system. 480/277 is never used in the residential systems.
Many older residential systems would have 240/120V, single phase 3 wire systems.
Hope this helps you cause.